They are, yes. But, the impedance of the earth path on a TT system from the installation end back to the supply Tx, can be extremely high as it is via the general mass of earth.

Also, in a TT system, the impedance between the MET and the general mass of earth (via the MEC & earth electrode(s)) and consequently the star point of the supply transformer can be very high (20ohms). In TN-S and TN-C-S this impedance is much lower (0.8 & 0.35ohms respectively) because the MET is directly connected to the star point of the transformer via the supplied earth or neutral conductors.

Now, ...Why didn't that come to mind to me earlier?? lol!! Yes i can see the point of the requirement now though, i still think it's advisable for all systems regardless. I can see far more benefits to having 4 pole isolation than 3 pole and a tied neutral, ....One obvious benifit is the total ease of testing.

You would also Need a 4 pole RCD device, if it were to be incorporated as forming part of the main switch/isolator or MCCB with earth fault facility!!

As i said before, i'll be sticking with the higher European requirement of a 4 pole means of disconnection to TP+N DB's... lol!!
 
Hi Hasel5

Single pole rcbos ?

What about them?

The Main DB is on a TN-C-S supply so sp rcbos protecting sockets is OK.

So the question is - is a single pole (only the live is switched but both poles sensed) rcbo acceptable for protecting a sub board which is TT?

Cheers
Pete
 
They are, yes. But, the impedance of the earth path on a TT system from the installation end back to the supply Tx, can be extremely high as it is via the general mass of earth.

Also, in a TT system, the impedance between the MET and the general mass of earth (via the MEC & earth electrode(s)) and consequently the star point of the supply transformer can be very high (20ohms). In TN-S and TN-C-S this impedance is much lower (0.8 & 0.35ohms respectively) because the MET is directly connected to the star point of the transformer via the supplied earth or neutral conductors.

thanks for your interesting and informative post lenny, i do understand much of what you are saying but could you provide a practical scenario so i may undersrtand the reasons why
 
thanks for your interesting and informative post lenny, i do understand much of what you are saying but could you provide a practical scenario so i may undersrtand the reasons why


These fault loop diagrams should explain it in a bit more detail.

It's all to do with the path the fault current has to take from the point of fault, through the installation, along to the supply Tx and back to the installation.

[ElectriciansForums.net] FARM INSTALLATION- First Time





[ElectriciansForums.net] FARM INSTALLATION- First Time




[ElectriciansForums.net] FARM INSTALLATION- First Time
 
Hi Lenny
May I clarify that the posts 19 and 20 relate to the earlier discussion about the use of 3 pole or 4 pole main isolators and are not an answer to my question on Single Pole RCBOs in post 20!
Pete
 
They are, yes. But, the impedance of the earth path on a TT system from the installation end back to the supply Tx, can be extremely high as it is via the general mass of earth.

Also, in a TT system, the impedance between the MET and the general mass of earth (via the MEC & earth electrode(s)) and consequently the star point of the supply transformer can be very high (20ohms). In TN-S and TN-C-S this impedance is much lower (0.8 & 0.35ohms respectively) because the MET is directly connected to the star point of the transformer via the supplied earth or neutral conductors.

:clap:Lenny I've gotta be fair to you mate, the way you answer peoples questions Rocks. :icon4:
 
Hi Hasel5



What about them?

The Main DB is on a TN-C-S supply so sp rcbos protecting sockets is OK.

So the question is - is a single pole (only the live is switched but both poles sensed) rcbo acceptable for protecting a sub board which is TT?

Cheers
Pete

Yes, its acceptable to use a Rcbo for protecting a TT circuit in some instances.

Regards Chris
 

Reply to FARM INSTALLATION- First Time in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

I should have written more…. 😫 😂😂
Replies
5
Views
1K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top