OP
Engineer54
They are, yes. But, the impedance of the earth path on a TT system from the installation end back to the supply Tx, can be extremely high as it is via the general mass of earth.
Also, in a TT system, the impedance between the MET and the general mass of earth (via the MEC & earth electrode(s)) and consequently the star point of the supply transformer can be very high (20ohms). In TN-S and TN-C-S this impedance is much lower (0.8 & 0.35ohms respectively) because the MET is directly connected to the star point of the transformer via the supplied earth or neutral conductors.
Now, ...Why didn't that come to mind to me earlier?? lol!! Yes i can see the point of the requirement now though, i still think it's advisable for all systems regardless. I can see far more benefits to having 4 pole isolation than 3 pole and a tied neutral, ....One obvious benifit is the total ease of testing.
You would also Need a 4 pole RCD device, if it were to be incorporated as forming part of the main switch/isolator or MCCB with earth fault facility!!
As i said before, i'll be sticking with the higher European requirement of a 4 pole means of disconnection to TP+N DB's... lol!!