Hi there just have a few questions regarding an agricultural installation.
1. Due to the existing installation being a TN-S earthing supply I understand that regulation 705.415.2.1 (note) that unless a metal grid is laid in the floor (which there is not) the use of a PME is not recommended ? This 3 phase supply also supply’s a house so could we keep the house on the TN-S and there for make the outgoing to the farm TT ?
2. Also 300mA main switch s type there for outgoing circuits 30mA unless it’s rated more than 32A 100mA protection?
3. When bonding/equipotential banding of the 3 phase consumer unit was to be turned into a TT there for when the earth rode is inserted into the ground we would then run all bonding cables to that with it being a TT system has all circuits to trip within 0.2
Thanks in advance
1. Due to the existing installation being a TN-S earthing supply I understand that regulation 705.415.2.1 (note) that unless a metal grid is laid in the floor (which there is not) the use of a PME is not recommended ? This 3 phase supply also supply’s a house so could we keep the house on the TN-S and there for make the outgoing to the farm TT ?