Just your thoughts on this one,extending some extra power points in offices,any problems coming off existing trunking ,conduit system with t&e 2.5mm.To be more precise,connecting onto 2.5mm single cables off ring man,with t&e cablng in a suitable enclosure,or condut like to like,easy to t&e at this stage cheers
 
Make your question out in proper sentences and it will be easier to understand. I think I know what you are saying and yes that is ok. But surely if you are doing this work you don't need to ask such basic questions
 
Why not use singles? 2 x t&e in 20mm conduit is a nightmare (assuming you are extending the RFC)

Also you are reducing CPC size if existing is 2.5mm
 
Last edited by a moderator:
Bloody silly question in this modern era, but what is wrong in following the existing installation, instead of B******ising it with an inferior extension installation??
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
fast fix
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
cliffed,
Replies
10
Views
1,097

Advert

TrueNAS JBOD Storage Server

Back
Top