Call out to a house, double socket in the far end of the kitchen has stopped working.
Questions to the home owner (my sister in-law btw):-
Has a fuse blown?
"Yes, this afternoon. I re-wired the fuse myself."
Do all the other kitchen sockets work?
"Yes, only the one that we plug the boiler into is broken, now we have no hot water or central heating. (combi gas boiler btw).
I plugged in my MFT into the socket and the readings were:-
L = 0V
N = 244V
CPC = 244V
Now going on what she said and the readings you have, what do you think has happened? Just to help you paint a picture in your mind:- (1) the socket is a spur so only 1 T&E going to it. (2) it has been spurred from another socket and the cpc is not terminated therefore no earth return path.
This is a strange one but it make logical sense once you know the answer.