You are using a mixture of visual observation, continuity testing and deduction.
You will be provided with a fault description.
e.g.:
light not working: this must be a disconnection on line or neutral, so test line continuity from supply to switch, across switch, from switch to lamp. test neutral continuity from supply to lamp. Where there is no continuity is the fault location.
RCD trips when light turned on: this is a connection from a live conductor to earth. test continuity between line and earth, break down the circuit until there is only one section that has continuity line to earth, this is the location of the fault.
MCB trips but RCD does not: this must be a short circuit line to neutral. Test continuity between line and neutral with no loads connected, break down the circuit until there is only one section that has continuity line to neutral, this is the location of the fault.
motor runs unevenly: this is (in the test) a phase lost. Test continuity from end to end of each phase the one that has not got continuity is the one that has the fault.