Quick drop in at a house on way home…. Customer couldn’t reset mcb for rfc.

Power off at board, outgoing cables disconnected… I was getting 200V between the neutral bar and the earth bar within the CU.

With the CU mainswitch on, I am getting a voltage on the disconnected live cables.
Have not disconnected the neutrals yet,

For now, I have left the cables disconnected, and the rest of the power on. Ran an extension lead to power the customers freezer. Will return to finish off tomorrow.

Looking at the picture below, the only other live circuit is the smoke detectors from the Wylex heating board to the right.
The rest of the heating board, and the all the off peak side of the teleswitch goes to redundant boards. It is so much more complicated than it should be.

What looks like a 3 phase head is a neutral, a live fuse, and a looped fuse which powers an advertising sign for a neighbouring hotel. Not metered, apparently.


[ElectriciansForums.net] Fault finding head scratcher.



Cross connection somewhere introducing a voltage onto the neutrals? Can only be from the smoke detector circuit.

However, this doesn’t explain the sudden cause of the breaker tripping.
Expect to find a smoking rodent in this one.
 
yep.... and it is an rfc... could continuity check end to end..... was just when the IR tester started squealing at me when i did L-E that i realised there was a voltage... not FULL supply voltage... thats actually sitting at 250V... but 200?

maybe appliances in circuit giving funny readings... I'm going to have to strip it down a bit to find the corresponding neutrals.
 
Yep you need to disconnect the whole circuit away from the CU and test again IR and ring continuity check if voltage is still on it first.
 
Last edited:
Almost certainly interconnected circuits. Switch off the other boards until it disappears then switch individual circuits from the offending boards. The tripping mcb is probably totally unrelated.
 
Almost certainly interconnected circuits. Switch off the other boards until it disappears then switch individual circuits from the offending boards. The tripping mcb is probably totally unrelated.
I would have said with an interconnection the OP would get full nominal voltage on the disconnected conductors. 200v or less could be lost neutral.
 

Reply to Fault finding head scratcher. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Could be damage to the N core touching the fabric of the building but the CPC of that cable is insulated from both. I.E. a screw clipping the edge...
Replies
3
Views
1K
  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
780
  • Question
That seems a very good shout. I’ll test that
Replies
2
Views
1K
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top