Hi all, new to the forum and hoping to garner some of your expert knowledge.

I live in a small 2 bed house and the main RCD on the consumer unit keeps tripping randomly.

There are 6 separate circuits and by elimination I've ruled out the lot except for the sockets (all on one ring).

Now I'm struggling to replicate or locate the fault, sometimes it goes off after a couple of minutes, sometimes an hour. I've tried unplugging everything and though I now have managed to keep it on for a couple of hours by removing an extension lead I'm not convinced it's the cause because the extension only has a lamp, macbook charger and iphone charger connected. It started this morning not long after we got up.

In addition I'm getting dodgy readings between live and neutral on the burglar alarm (2000 ohms) but this is on the lighting circuit and it still tripped when I removed the fuse for the alarm and had the lighting circuit turned off.

I'm stumped and though I have a decent multimeter (fluke) and used to work as a linesman I'm struggling on how and what to test.

Any advice or pointers would be welcomed with tears of joy because I'm well out of my depth here. Once the fault is located I can fix it a doodle but I just need to find it first.
 
removing the fuse is not going to solve the fault,sound like N/E FAULT in the circuit ,which circuit?

The burglar alarm is on the upstairs lighting circuit but the main RCD still tripped when this was isolated via it's individual RCD which led me to believe it wasn't that circuit at fault.
 
Mice, rats, cable partly burnt by downlight, cable burnt by central heating pipes, leaky roof, leaky radiator, stray nail into cable, faulty light fitting, faulty appliance......

could be pretty much anything.
 
how about disconnecting one circuit at a time from the CU and leave for a few days each time? you will have to flick the MCB off and disconnect the associated neutrals. it will take some time but without an MFT the only way to go
 
Sorry to say it, but the easiest and quickest way to sort it is to get a spark in, might only take him 5 mins.
Best bet, is, unplug everything u r not using, and I mean everything, and I mean physically remove the plug, see if the problem goes away, if it then still goes off, unplug everything, make sure no neons, switches etc are on
if u still have a problem it's on the circuit, u need a spark, if it goes away, plug one thing in at a time till u find the culprit
 
Last edited by a moderator:
The rcd is between neutral and earth. Isolating the mcb would make no difference, it could still trip

An RCD that complies to BS61008 does not have a connection to earth, it has connections to live and neutral. Some manufacturers put earth connections on RCBOs but they are not mandatory if you check BS61009. An RCD detects an imbalance in the current between live and neutral.
There is no relationship between neutral and earth on an rcd and they were devised to overcome the problems of earth faults and ELCBs.
If I am wrong please tell.
 
Your a bit late!
Yes I know, I was trolling for inspiration on a really weird RCD fault and found this thread. Wishful thinking as the property has old and overloaded wiring, wires touching pipes all over the place, leaks in a flat roof, ancient appliances and scatty tenants from Goa.
I think prayer is my only hope on this one.
 

Reply to Fault Finding Help Please, Random RCD Tripping. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
357
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
910
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
691
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top