Ok chaps, a customer calls you saying he has a 'tripping problem' on his CU. Apparently it is totally random and no rhyme nor reason to it. No work done recently etc etc but the RCCB trips every now and then and the guy is worried as he is going on hols soon and naturally doesn't want fish to die etc should the power go off.
Now, where would YOU start? I reckon best way is to change RCCB for a new one and then go from there but what are your thoughts chaps?
 
Try to isolate the circuit that's causing the tripping by leaving each breaker in turn off would help narrow it down. Or try unplugging appliances one by one. But if the tripping is very spurious this is a long job to prove what the problem is.

I'd start with unplugging everything and doing the continuity / IR and RCD tests on the wwiring system alone to see if that gives any clues. Also, consider how it's wired. Our RCD used to spuriously trip with no appliance conclusively to blame, but we suspected something or other in the kitchen. Wen the buliders did our kitchen some 15 years back they wired it themselves. They took two radials off of the ring, and we were plugging all of the big power users into one of these radials. A new ring in the kitchen solved that one.

If the tests shed no light, I'd be inclined to suspect kitchen appliances, or items with a motor as the most likely culprits. Not easy I know!

But if his concern is the fish, then does he have any non - RCD supplies that have sockets on them?
 
Last edited by a moderator:
Have that problem with the old stone walled houses. Walls get very damp and cause nuisance tripping randomly.
I would do Insulation resistance test. You could try Earth leakage clamp on each circuit if you have one.

Have also had the problem several times when washing machines run and ten mins into cycle or so when the heaters come on...the trip goes. Common fault with heating elements in a washer.
 
It's a difficult one as from what you say there is no common denominator with regard to why or when it trips. If it is a true intermittant fault even using a clamp may not show where they problem lies initially.

If the customer would accept the cost etc you could always replace the cu with one containing rcbos and atleast you could then identify the faulty circuit when it tripped.

This is going to be a bit of a brain tease:eek:
 
Expensive option changing the board for one full of RCBO's but I suppose 2 days scratching my head trying to find the fault is just as expensive. Don't have an earth leakage clamp either:(
 
Hi, I have the same problem now and again intermittent tripping. Now I only found out it was the RCD it's self found it by a ramp test with my new meter, tripped at 15mA, it mainly trips when the kids plug in the power supply for the laptop, this can cause a residual current enough to trip sometimes. I will change the RCD soon, it's just extra sensitive for now.
 
I get this problem a lot where i am as a lot of the houses are made of Portland stone that gets very damp. I start with a ramp test on the RCD and if OK then IR test the whole house 95% of the time i find the fault by these two tests.

Failing that i would turn every other circuit other than his fish tank of. Someone must be coming in to feed the fish so they can check the RCD has not tripped.
 
Have had this exact problem.RCD on whole house. Changed RCD to no avail, Meggerd everything, set about PAT testing appliances and found two with a small amount of earth leakage that on their own would not trip the RCD, but together they did. RCBO's would have narrowed it down a lot quicker.
 
even if the problem doesn't occur all the time, an ir test would indicate which circuit was more likely at fault. if this is a socket bearing circuit a temporary extension lead supplying the fish may prove useful. ( what does he have ? Electric eels?)
 

Reply to Fault finding help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top