Hi all. Just been to look at a job that was recently done by another electrician, can't fault the work other than he has yet to provide the client with any certificates and no fly lead on the armoured cable supplying a sub mains board! It's a summerhouse being used as a gym/storage. It has a sub mains consumer unit with one ring final and one lighting circuit. Basically the ring final circuit and the RCD at the main consumer unit in the house is tripping when the lights are switched on and the treadmill is running. The treadmill is from the US and has a litefuze lt5000 step up/down voltage transformer to power it up. Other than the treadmill there is only a fan plugged into the ring main. What I am wondering is could it be the transformer that is causing the breakers to trip, anyone else encountered this issue? Also to note is it does not trip when the lights are switched off, only when both the lights and treadmill are on, which has got me slightly baffled. I have carried out a Zs test but no insulation tests thus far.
Any suggestions appreciated!