Fault finding problem | on ElectriciansForums

Discuss Fault finding problem in the Talk Electrician area at ElectriciansForums.net

G

Gavthesparky

I am having some problems at discovering a wiring fault between neutral and cpc on a ring circuit. The RCD dedicated to the various socket circuits at this house trips as expected because of the fault but also trips when the downstairs lighting circuit which is in the same board but not protected by the rcd is energinised. I have disconnected line, neutral and earth of the offending socket circuit from the board and now the lights are not affecting the RCD but I am still getting a reading of 1V in the dead sockets. Any ideas to what might have caused the problem, and also ideas on how to find the fault without pulling the place apart.
:confused:
 
sounds like a borrowed neutral. i.e a neutral taken from a circuit on the protected side to a circuit on the non protected side. or vice versa. landing lights are the most common cause. neutral from upstairs cct. and live from downstairs cct.
 
I am happy that the neutral is wired correctly at the board. I think it is being shared elsewhere along the circuit. Odly this installation has been working fine for the last 4 years from commision then pop the washing mackine trips the RCD and suddenly a whole load of problems happens.
 
Is this happening after a board change or just something you've been called out to. The one volt is probs just an induced voltage from cable running near each other.
 
If more than one circuit starts to get affected, it may be worthwhile carrying out a PIR on the installation.

I had a situation like this once where the shower install was at 136V to earth, it turned out to be damaged insulation on some switchdrops on another circuit. Individual testing of the circuits is the best way to find these problems.
 
are both lighting circuits on the same rcd? if you put them on the same side and the tripping stops that is a sign that it is a borrowed neutral- it is not however a long term solution.

Have you tested the rcd?
 
Last edited by a moderator:
This is something that I have been called out to. I have managed to get the lady up and running with everything except the offending circuit which for you interest is wired in a 16th edition style with only the socket circuits wired through an RCD. I am returning on Wednesday to do a PIR.
 
I am having some problems at discovering a wiring fault between neutral and cpc on a ring circuit. The RCD dedicated to the various socket circuits at this house trips as expected because of the fault but also trips when the downstairs lighting circuit which is in the same board but not protected by the rcd is energinised.:confused:

What have you done to confirm this fault - insulation resistance or continuity? If you are getting a low continuity reading you can check from either side of the ring and you can then use the resistance value to calculate the approx distance to the fault.

Are you certain it is not a dodgy appliance still on the ring?
 
So far all I have done is an insulation test which came back as 0 ohms between neutral and cpc. I feel sure that I have now isolated all appliances and the next plan is to do as you suggested and do a continuity test between the two offending cables to try and locate the fault.

Thanks for the feedback
 
The chances are its a trapped neutral in the socket check on continuity and see if you get a reading if you do , and you have a plug in socket for you meter plug the neutral into live and earth into earth as you would normally then go round each socket and test at the socket the lowest reading at a socket could be where your fault is , could also be in a jb under the floors , unless its concrete that is, once you find the fault re do your IR using the normal methods
 
So far all I have done is an insulation test which came back as 0 ohms between neutral and cpc. I feel sure that I have now isolated all appliances and the next plan is to do as you suggested and do a continuity test between the two offending cables to try and locate the fault.

Thanks for the feedback

might be a silly question, but did you dis. the neutrals from the CU terminal block when IR testing?
 

Reply to Fault finding problem in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
359
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
668
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
561
  • Question
I misread it.
    • Like
Replies
13
Views
832
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks