underpar12

testing ring main on a house about 35 years old.one ring main for all the house plus extension plus garage. no continuity on phase conductor, dead short on nuteral to earth I,R test . concrete floors down laminate up.checked all skts for loose conections,no luck. split ring on to two 20amps diferrent sides of r,c,d. trips when a load is on, mutiple rings , back to one 20amp start disecting ring ,suspect lots of jbs,any advise or sugestions many thanks.already disconnected garage to check separetly.plus all spurs visable.:mad:
 
If you have split the rings....did you also pick sockets at which to split neutrals and earths otherwise the RCD will see a "borrowed neutral" between the two radials and both RCD's will trip.
 
Take a trailing lead from one of the ring legs at the consumer unit and using an adator or plug ,test the sockets for contiuity of that leg,keeping a note of their location(dont forget switching the sockets on :))
Do the same with the other leg and compare the located results
This should indicate roughly where the lost live is located
Reinstate legs at consumer unit and concentrate your testing in the end of radial locations

You have my sympathy,ring continuity losses can make you go giddy, going around in circles with it all

By doing the above,if you do have to make 2 radials,you now know whereabouts the split has to be made on the neutral conductor as well
 
Tell your customer they`re spoilt for choice - laminate up or ceiling down
Seriously , you have to locate where the faults are on the legs, then disconnect the damaged sections and see what that leaves working on 2 radials, if they`re not happy with losing x number of sockets then back to my first line
 
only had the visit because an old 3036 fuse ,when blown sparked caught the coats on fire and then melted all the cu in the cupboard.all the best jobs?
 

Reply to fault finding ring main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top