i fitted a new rcbo to a ring over a year ago and now its tripping so naturally its my fault. Switched everything off

Ramp tested rcbo 28ma
rcd test 1x 34ms 5x 28ms
ring continuity
L - L O.78 OHMS
N - N 0.77 OHMS.

Old PME system so no cpc its the steelwork.

IR 89.3 Mohms PN >E (GN3 method 2)

still a fault and my mates pat testing the gear tommorow any ideas???
 
mmm
upgrade protection on an existing circuit and later it trips out..
id say good job they got you in..coz that new protection could have just saved thier lives
its fault protection init.
 
Last edited by a moderator:
Did you ask them if they were switching something on at the time it tripped or if anything was running ie washing machine / dishwasher I once got a O yes we were plugged in that old standard lamp to see if it was working so since your here could you look at it for us.

Answers on a postcard please
 
kettle..washing machine...old microwave....hob...water heater....my best one was a boiler which tripped each time auto ignition kicked in(well almost each time) and it was only 3 years old..
 
Hair tongs, straighteners etc, the cable cores crack where they go into the body of the appliance, outer insulation looks fine though. same with Irons, toastie machines and kettles. Another good one is water in the connections in base of the of cordless kettles...this happened in my house a while back. :eek:
 
Last edited by a moderator:
Was the testing done with loads applied ?

The Rcd/Rcbos may be operating with accumalation of leakages from various sources
Perhaps testing with the loads applied might unviel something
 

Reply to fault on a circuit. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
984
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top