I had a 10 minute look at an existing fault yesterday as walking out of a customers house as it was way past beer o'clock, the circuit is from a dual RCD board. Serves lighting in a loft conversion with balcony (outside lights) en suit, downlights shaver socket, bathroom fan and central pendant.
Tested IR which was very low at 13.44MΩ between joined live/neutral and earth and no continuity on earth and neutral and live conductors.
Energised circuit and everything was fine, then decided to test RCD and then the circuit tripped the RCD, both RCD's are ramp testing okay. Now continuity shows resistance between live/neutral and earth around 66Ω.
Thinking a nail through a cable/neutral fault somewhere but trying to work out in my head why it all energised okay and then tripped and fault re appeared during the RCD ramp test? Any suggestions or previous experience of this from anyone? (Going back monday morning!)