C
claret73
Had a Minor, Non Notifiable to do for a friend. Moving 2x sockets in the bedroom. After looking at it and from a response on here, took new legs up into the loft (it's a top floor flat) and joined in a 30A JB to the Incoming legs off the circuit.
Came to test it, as was supplying a BS7671 MW Cert. (I guess this will smack of hindsight in that I never did sample tests first) I did a continuity check end to end and had no reading on the Line conductors. Cross linked legs, L-CPC & did R1+R2 at every point. Got readings on the Meter at each outlet. Confused as continuity on the Line was effectively showing open circuit?? Did IR at 250V as a starter and got over 250MOhms on L-E, N-E. L-N was showing short (possibly a Neon that I hadn't picked up?) at 500V all at 0.35MOhms...even did L&N Together to earth and got same reading.
Did ZS and got 1.10 Ohms for a 32A 60898 Type B, so within Max ZS. Did RCD disconnection and that was around 30.5ms for 1x.
So, I'm getting confused on the Continuity, the fact it's showing none, yet get a reading & voltage at every point...IR Readings are a worry. Nothing plugged in. The only thing I can put to it was, on the way out I noticed a loose socket, so offered to tighten it up. The Pin wasn't in at one side so removed it. The opposite Pin had gone through 1 Line Cable and so snipped this off & re-terminated into socket. I need to clarify that this may have had a changed reading or not??
Finally, the Earthing Conductor is 6.0mm for a PME & Equipotential Bonding is 4.0mm (which really I should look to upgrade). The 6.0mm using the adiabatic not having measured Ze, could I take Max Ze at 0.35 to get Fault Current? Would this be at it's worst case using Max Ze?
Any thoughts on any of this?? I've tried asking the Electrician I'm working with but wasn't either convincing or too obliging...
Cheers!
Cheers!