Hi all,

I've a question about fault paths. I understand that the earth fault loop impedance is measured during testing so that it can be compared to the maximum value in the regs and adjusted to 80% to compensate for temperature under load conditions, but what if the fault is a short circuit ie. line to neutral, what test is done to ensure that the protective device will operate within the required disconnection time?

Thanks
 
the EFLI values are set assuming a L-E fault of negligible impedance ( dead short ), to ensure disconnection times in the event of such a fault.
 
Hi all,

I've a question about fault paths. I understand that the earth fault loop impedance is measured during testing so that it can be compared to the maximum value in the regs and adjusted to 80% to compensate for temperature under load conditions, but what if the fault is a short circuit ie. line to neutral, what test is done to ensure that the protective device will operate within the required disconnection time?

Thanks

Good question. We make a big thing about measuring R1+R2 and Zs, to ensure that the earth fault path is of low enough impedance to operate the protective device in a short enough time. There's much less emphasis on measuring R1+Rn and Z line (line impedance). I do the Z line check at the end of the circuit at the same time as I'm doing the Zs test. If it's higher than the Zs reading, of course I'd investigate (hasn't happened yet).

Anyone know if there's a 'proper' symbol for the line impedance (like Zs for earth loop)?
 
Hi all,

I've a question about fault paths. I understand that the earth fault loop impedance is measured during testing so that it can be compared to the maximum value in the regs and adjusted to 80% to compensate for temperature under load conditions, but what if the fault is a short circuit ie. line to neutral, what test is done to ensure that the protective device will operate within the required disconnection time?

Thanks

Just hope the MCB or RCBO is not a chinese copy!!
 

Reply to Fault paths question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top