swaley

-
Joined
Mar 24, 2018
Messages
60
Reaction score
34
Location
Essex
got called out to a job yesterday. Upstairs ring Mcb not staying on. Done a quick visual took all sockets off didn’t notice anything out of sorts. All appliances unplugged only other thing on ring is boiler programmer off a fuse spur. So I split the ring did IR and one side was showing a low reading. I energised the good side and starting the tedious process of trying to find the culprit on the dead side. I came across 1 leg between 2 sockets which was giving me a reading of o.52 ohms IR. so I disconnected the link between and energised both sides. Voila mcb stays on. My concern now is I have a socket in hallway and boiler programmer with no power. Even though both legs are in board? And 2 sockets in another bedroom showing 60v output. I’m baffled didn’t have time to get boards up need to go back. Surely by disconnecting 1 faulty link I would in principle have 2 radials?? tenant just moved in recently new carpets fitted and it’s been intermittent tripping. Any ideas guys
 
What do you mean “Voila MCB stays on” what was the IR of the 2 legs once you disconnected the faulty legs you found?

What meter did you use to get a IR of 0.52 ohms?

Did you leave both legs connected the same OCPd?

What size was the OCPD?
 
0.52 isn't low enough to trip a mcb imho...

Go back and confirm your findings, then investigate more

That's what I would do...

Edit. What was the IR of the disconnected part of the circuit?

And did the tripping start after the new carpets were fitted?
 
What do you mean “Voila MCB stays on” what was the IR of the 2 legs once you disconnected the faulty legs you found?
Because didn’t switch on prior
What meter did you use to get a IR of 0.52 ohms?
Fluke mft
Did you leave both legs connected the same OCPd?
Yes
What size was the OCPD?
Didn’t switch on prior. Fluke mft. Yes & 32a
 
0.52 isn't low enough to trip a mcb imho...

Go back and confirm your findings, then investigate more

That's what I would do...

Edit. What was the IR of the disconnected part of the circuit?

And did the tripping start after the new carpets were fitted?
The IR was o.5 at disconnected part. I’m going back Saturday now so will update when I find out a little more. A nail from carpet gripper is always a possibility
 
So you have left 2 radials on a 32amp MCB? What size cable was it?
What range did you have your meter on to get that reading for the IR?
No spare ways on board also didn’t have a spare 16mcb on van. 2.5mm. Sorry should of mentioned 250v range on IR. didn’t test at 500v. I’m going back saturday
 

Reply to Fault problem with up ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
989
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top