got called out to a job yesterday. Upstairs ring Mcb not staying on. Done a quick visual took all sockets off didn’t notice anything out of sorts. All appliances unplugged only other thing on ring is boiler programmer off a fuse spur. So I split the ring did IR and one side was showing a low reading. I energised the good side and starting the tedious process of trying to find the culprit on the dead side. I came across 1 leg between 2 sockets which was giving me a reading of o.52 ohms IR. so I disconnected the link between and energised both sides. Voila mcb stays on. My concern now is I have a socket in hallway and boiler programmer with no power. Even though both legs are in board? And 2 sockets in another bedroom showing 60v output. I’m baffled didn’t have time to get boards up need to go back. Surely by disconnecting 1 faulty link I would in principle have 2 radials?? tenant just moved in recently new carpets fitted and it’s been intermittent tripping. Any ideas guys