Yesterday I was changing a board and encountered the following faults when I livened it up;

RCD 2 ok, RCD 1 with the upstairs lights and down stairs ring on, both MCB,s tripped the RCD. I found one desk light I'd missed on initial testing and took it off the ring. RCD now ok. Assuming the reason for the upstairs lights being a borrowed neutral I put put both the upstairs lights and downstairs lights on the same mcb and neutral bar on RCD 2 and all ok.

Happy that I'd worked out the faults, a borrowed neutral and faulty desk lamp I went upstairs to live test and when I turned on the bathroom light it tripped out the other RCD (RCD 1), not the one it was on (RCD2). I turned every MCB off on RCD 1 and tried again, even with nothing on it it tripped.

Then I did an RCD test on the downstairs ring (RCD1) and for x1 I got >400ms. I changed the RCD incase it was faulty but the replacement did the same.

My Ze was 0.2
PFC was 0.76
Insulation resistance was ok on the rings, but the lighting was about 1 doing a soft test at 250v (there are a few dimmers etc)
oh, and I also got an open circuit on end to end neutral on the downstairs ring

Anybody got any ideas why the other RCD would trip when you turn on the bathroom lights, I really dont know where to start.
 
IR test each circuit L-E and N-E separtely and disconnected from the db one circuit at a time....also IR test each circuit while disconnected from N to the other Neutrals still connected which will indicate any borrowed neutrals between circuits.....Double check each N is identified to the corresponding live and connected to the correct N bar....Double check the N links from the RCD's to the bars are correctly connected
 
I checked each neutral was connected to its corresponding mcb, so dont think this is the cause. Wirepuller, how will a seperate insulation resistance test between N and L and N and CPC tell me if there is a borrowed neutral, and what reading should I look out for?

***Just re-read, do it between neutrals - great idea
 
Last edited:
I would probably turn everything off apart from lighting circuit discconnect the neutrul for that circuit and turn bathroom light on. if it trips then its either a borrowed neutrul or earth problem.
 
oh, and I also got an open circuit on end to end neutral on the downstairs ring

Anybody got any ideas why the other RCD would trip when you turn on the bathroom lights, I really dont know where to start.

Possibly just a poor termination at a socket, check neutral continuity with a wandering lead to find it.

Its a good idea to do all the testing before you actually change the CU so you don't get all these unpleasant surprises at the end of the job ;)

edit might be worth checking in the loft for connected loads if it is not your place eg tv aerial amplifier, spurred sockets, lights etc.
 
Last edited by a moderator:
Its a good idea to do all the testing before you actually change the CU so you don't get all these unpleasant surprises at the end of the job ;)

Not getting prickly Pushrod but I did all the dead tests and only really got an open circuit on the neutral and low ins res on the lights. Neither of which made me think I was in for the faults I found. I didn't just lash it up and hope for the best.

Thanks for your other suggestions though!
 
You say there is 2 light circuits are they in T+E or are they singles ? Also if you can take the RCD out of circuit so that you can confirm that the circuits are correct.

The thing is it a shared neutral or has someone commoned the neutral in the field ?

Must admit I have never come across a shared neutral is this an english thing ?
 
Not getting prickly Pushrod but I did all the dead tests and only really got an open circuit on the neutral and low ins res on the lights. Neither of which made me think I was in for the faults I found. I didn't just lash it up and hope for the best.

Thanks for your other suggestions though!

Apologies if it sounded smug or like a smart a*** , not meant that way :)
 
oldtimer;156582 Must admit I have never come across a shared neutral is this an english thing ?[/QUOTE said:
just a term to describe the pre RCD practice of taking the neutral back to the CU on a different circuit to save a bit of cable. Quite common on the stairway lights in older properties.
 

Reply to Fault(s) when changing a 3036 to RCD CCU in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
186
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
984
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
801

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top