Just so I've got it straight in my head, in this 32amp breaker you have both ends of a ring (2 cables 2.5mm) and then some one has also added a spur, another 2.5mm phase, 3 cables into one breaker?
If this is the case, the ring is protected by the breaker. the spur is not, 27amps max for 2.5mm.
Obviously if you have one socket you can only draw 13amps, two sockets and your close to fire with no chance of the mcb tripping? Am I thinking along the correct lines?