Just so I've got it straight in my head, in this 32amp breaker you have both ends of a ring (2 cables 2.5mm) and then some one has also added a spur, another 2.5mm phase, 3 cables into one breaker?
If this is the case, the ring is protected by the breaker. the spur is not, 27amps max for 2.5mm.
Obviously if you have one socket you can only draw 13amps, two sockets and your close to fire with no chance of the mcb tripping? Am I thinking along the correct lines?
 
It is absolutely fine to spur from the cu see pg 362 in your 17th edition regs if you dont have it maybe its time you updated.read the part about an unfused fuse spur.

Just so I've got it straight in my head, in this 32amp breaker you have both ends of a ring (2 cables 2.5mm) and then some one has also added a spur, another 2.5mm phase, 3 cables into one breaker?
If this is the case, the ring is protected by the breaker. the spur is not, 27amps max for 2.5mm.
Obviously if you have one socket you can only draw 13amps, two sockets and your close to fire with no chance of the mcb tripping? Am I thinking along the correct lines?

this is what they call diversity theres not a great chance it will draw 26a unless you used say 2 heaters and then the regs advise if you were to use electric heating you should wire a radial just for that and not put it on the ring as a ring in thefirst place is designed to share the load, its also the same with ceiling pendants technically th0.5 flex supplying the light is protected by a 5/6 or even a 10 amp fuse and we all know the smallest we can use is a 1.0mm but we also know a light bulb wont use that much current so diversity is applied.
 
Last edited by a moderator:
you can have as many sockets in a radial circuit as you want

but any more than one s/o on the radial circuit you create then you need to protect the circuit by using fused spurs.

as for the disconnected phase being 'live' at 170v, this is very unusual. i'd unplug everything from the circuit (incase for some reason paranormal reason there is any abnormal capacitance, voltage sources like batteries there) i'd also disconnect and do some extensive IR tests to see if you've got any sort of leakage. i can say i've not come across anything like this before, except in emergency power/lighting supplies

let us know how you get on with this, i am intrigued
 
hi thanks for the comments, it is on a lighting circuit, but the batt in em lighting should have nothing to do with it. this has never proved a prob before or on any other similar circuits in the building.

im looking into it and will let you all know :)
 

Reply to faults, cables spur from mcb. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
623
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
780
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
796
Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top