Faulty light switch causes shower pump to start up | on ElectriciansForums

Discuss Faulty light switch causes shower pump to start up in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 21, 2012
Messages
40
Reaction score
5
Location
Leeds
Went to look at a job where the customer was complaining of his bathroom lights working intermittently and also that sometimes he was hearing ‘a loud noise like thunder’ when he turned his bathroom lights on.


Found that the connection in the light switch was ropey, and when the switch is partially open - i.e. when it is arcing across the contacts in the switch, the shower pump in the bathroom cupboard starts up for a couple of seconds!


My question for the kind users of this forum is… WTF?


The shower pump is on the same circuit as the bathroom lights but is obviously wired with permanent L+N (not into the switched L+N feeding the bathroom lights).


The shower pump is starting up for a couple of seconds even though the shower is not running. Otherwise the shower pump comes on with the shower when it should, and works fine.


There’s no RCD on the circuit as it’s an old Wylex. Megger values are fine. I checked for wires wrapped round pipes or anything like that and all looks fine.


Any ideas why this would happen? Should I just replace the light switch and not worry about it?


Thanks in anticipation.
 
As usual, what test results did yo get when you tested the circuit.

Seems to be an echo in here today.

sorted that for you D
 
Well go back and do it, what about L-N? Continuity of all conductors? These are basic tests that should take about a hour to carry out.

please don't tell me you have been to have a look and decided you need to ask on here as you don't know what you are doing?
 
Well go back and do it, what about L-N? Continuity of all conductors? These are basic tests that should take about a hour to carry out.

please don't tell me you have been to have a look and decided you need to ask on here as you don't know what you are doing?

a tad harsh before beer time?
 
Harsh?

The OP claims to be a spark yet doesn't even do the basic testing on arrival on site, just a quick LN-E insulation resistance test, bet they charged for that test too. Now that's harsh on the customer.
 
Tel, well spotted hawk eye and I am with dillb on this. I cannot imagine going to one of my regular customers on a fault and saying, Can you please wait while I go on a forum and ask the lads what they think it might be. They would never let me back in the place.
It seems everybody these day's wants spoon feeding! instead of testers I think some people on here would be better off with a BIB.
And for the record it is now officially beer o'clock....speaking of which!!!
 
Well go back and do it, what about L-N? Continuity of all conductors? These are basic tests that should take about a hour to carry out.

please don't tell me you have been to have a look and decided you need to ask on here as you don't know what you are doing?

I used the time I had available to ascertain that the switch was faulty, megger the circuit LN to E and look at the wiring in the loft. I couldn’t replace the pull-switch as I didn’t have one in the van.


Rather than charge the customer for an hour’s worth of testing, leave him with a faulty switch anyway, and make myself late for my remaining jobs that day, the sensible course of action appeared to be to go back when I had more time, a replacement switch, and the thoughts of the helpful people of this forum.


If you don’t think that was the sensible course of action then it would be useful to know why.


It would be even more useful if someone could help with the queries in my original post.
 
I used the time I had available to ascertain that the switch was faulty, megger the circuit LN to E and look at the wiring in the loft Why look at the wiring when testing it with the proper test equipment will tell you all you need to know about it?. I couldn’t replace the pull-switch as I didn’t have one in the van.


Rather than charge the customer for an hour’s worth of testing, leave him with a faulty switch anyway, and make myself late for my remaining jobs that day so why didnt you say you were busy and available another time when you wouldnt be rushed? , the sensible course of action appeared to be to go back when I had more time, a replacement switch, and the thoughts of the helpful people of this forum. Its only helpful when you can supply all the test results, not just a quick LN-E IR test.


If you don’t think that was the sensible course of action then it would be useful to know why.


It would be even more useful if someone could help with the queries in my original post. You will recieve help, but only once you have done all the testing as previoulsy stated.

Replied as relevant.

This forum isnt a one stop remedy shop, if you arent competant/confident in fault finding, its OK but at least admit it, none of us are perfect but really there are so many basic things to do before asking on here for some help.
 

Reply to Faulty light switch causes shower pump to start up in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
438
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
746
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Article
This is an RSS feed of thread: Why is my pumped shower suddenly slow in starting? Content of the thread: Not been on here for ages, got a lot of...
Replies
0
Views
225
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top