Domestic installation, rcd tripped on supply to garage which then feeds a barn 25 metres away via swa. supply cable to garage is swa and tests out fine on insul res and continuity as does swa to barn. connect any load to con unit in barn even with no earth and rcd trips? Circuits in barn show healthy insul res readings? any ideas chaps?
 
Is this a brand new installation, or an existing one that has mysteriously started to have this problem.

If it's new, it sounds like a neutral in the wrong busbar, or neutral link not taken out between busbars in an RCD consumer unit.
 
as others have said do a ramp test on the rcd. If all is well try disconnecting each circuit individually and then loading the installation to rule out the possibility of parallel paths.
 
yeah test button is functioning

That is NOT how you test an RCD.

The test button is a very basic functional test.

From the sound of it "someone" has done a board swop and mixed up the neutrals.
That "someone" also has not done the required tests on the existing and the altered installation.
 
Anything plugged in?

Got called back to a CU change, which I had completed on Friday, on Saturday morning - customer had tripped the RCD when plugging in a 4 way extension. I took the cover off the plug of the extension and the N-E were reversed. He did look a tad embarrassed!
 
neutral connection for a lighting cct found to be in the wrong bar on investigation, have done new checks for customer and circuit is behaving itself. rcd tests were o.k. thanks
 

Reply to Faulty rcd? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top