C

chris troman

At a job where using the shower trips the main rcd and two rcds under it (not on shower circuit). rcd test trips the lot at 1/2 current. When i isolate the main rcd from all circuits after it it fails to trip even at 5 x current. I suspect the main rcd to be at fault. can any one confirm this ? Also I have been told that rcds in line can affect each other. Could the two rcds away from the consumer unit have contributed to the failing of the main rcd, which was fitted after and is about 7 years old. thanks chris
 
test each RCD with any others in series bridged and no circuits connected. if they trip correctly, then i suspect you have a N-E fault somewhere on the installation.
 
test each RCD with any others in series bridged and no circuits connected. if they trip correctly, then i suspect you have a N-E fault somewhere on the installation.
please re read the original post. when the main rcd is isolated from the circuits it fails to operate even at five times the rated current. I would assume in anyones book that is not good. the other point is that I suspect the other rcds (originally fitted to the installation before the new consumer unit was added with an rcd covering 4 circuits) may be damaging the main rcd. thanks chris.
 
RCDs cannot cause harm to other RCDs no matter how they are connected.
So long as the main RCD is correctly connected to the power supply and the RCD testing is done correctly then if it fails to trip under test then it is faulty, however if there is a fault in how it is connected or how the testing is done then this may not be the case.

RCDs that are connected sequentially especially if they are of the same rating (e.g 30mA) will, under fault conditions, trip randomly, i.e. it will not be possible to tell which one (or both) would trip in the case of a fault.
RCDs connected in parallel will not affect each other, although incorrect connection of the RCDs may cause tripping of another device.
Also it is possible that if a current spike occurs under fault conditions that this may affect the supply and cause an imbalance sufficient to cause an adjacent RCD to trip.
 
Describe the arrangement of these RCDs for us so that we can understand how they connect to each other and what they each protect along with the rating of each one.

Having RCDs connected downstream of other RCDs will not damage them, I've done it many times with no problem whatsoever.
 
please re read the original post. when the main rcd is isolated from the circuits it fails to operate even at five times the rated current. I would assume in anyones book that is not good. the other point is that I suspect the other rcds (originally fitted to the installation before the new consumer unit was added with an rcd covering 4 circuits) may be damaging the main rcd. thanks chris.

are you sure this main RCD is not 100mA and /or time delay?
 
please re read the original post. when the main rcd is isolated from the circuits it fails to operate even at five times the rated current. I would assume in anyones book that is not good. the other point is that I suspect the other rcds (originally fitted to the installation before the new consumer unit was added with an rcd covering 4 circuits) may be damaging the main rcd. thanks chris.

With the greatest respect, you should answer the subsequent posts to your less than detailed post! I'm still not sure what you mean!
 

Reply to faulty rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
438
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
746
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
514
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top