I

Innominata

Hi Guys,
Calling out to look at a faulty shower.Customer informs me that he has measured only 70v at the pull switch.Any ideas apart from faulty switch.Thanks
 
Yes process of elimination.

Customers says 70 volts ??? Dingy this for a start

Switch shower off at isolation switch then check if the board side is sound ie are you geting a supply
then move on to shower itself.

Mind ask the time honoured question that is have you had this renewed recently as the old 6kw gets chucked out and the 9kw gets put in only problem is the wiring is not rated for this.

other than that good luck
 
My money is on a burnt out neutral in either CU, pullswitch or shower. Just a guess but an educated one from experience;)

Cheers........Howard

I'll have a fiver on that too.....(pullswitch is a clear favourite....fit pullswitch....tighten connections...wrestle 10mm's back into box,wont go....wrestle some more,finally manage to get them back,previously tight connections now loose as hell...40 amps through loose connection.............:eek:.)
 

Reply to Faulty Shower in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Thanks for the reply, yes the plumber replaced the fuse and it blew again. Replacing the pump, or the PCB is circa £250 each so it looks like the...
Replies
2
Views
1K
  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top