M

mark1977

I have installed two lighting points in a garage through a FCU connected to a ring final circuit. When testing the installation would I treat the FCU as a distribution board and add my R1 + R2 from the furthest light to the FCU? Or would I need to include the R1 + R2 of the ring circuit too?
 
I was hoping to get an R1+R2 reading to add to the Ze to try and avoid working live (EAWR and all that!) How would I test it if I wanted to go down this route?
 
do R2 reading!!! much more simple!! connect ya Lead to FCU screw and then use a wander lead (or a piece of nulled cable) and other lead to Earth Terminal in light!!

Simples...
 
I was hoping to get an R1+R2 reading to add to the Ze to try and avoid working live (EAWR and all that!) How would I test it if I wanted to go down this route?

Cross-connect line and cpc and take reading at FCU. Then connect line and cpc at FCU to your light. Add this to other reading and that will be total R1+R2, and add to Ze. Don't forget to include your switch returns.
 

Reply to FCU off ring final circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

  • Question
Thanks for the advice.
Replies
11
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top