Filling in this part EICR | on ElectriciansForums
Discuss Filling in this part EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
cliffed
Worcester
The bit in red does this apply to the DB that supplies the DB…or the actual DB not connected to the origin…just had a senior moment
  • [ElectriciansForums.net] Filling in this part EICR
Cant open it, but if it’s the bit I think, it’s the schedule of test results and you are listing circuits and results for a given DB. If that DB is not directly connected to the cutout then fill out the bit in the box above saying what is feeding it and the other bits about the circuit supplying it and the protective device of the supply circuit.
Cheers definitely the supply curcuit, pic still not opening.
A bit puzzling the DB that it supplies, there’s then no where to put the Zs of that DB,if required
I suspect that there actually is.
I don't know if it helps but here's another couple of format forms that might clarify the one you are looking at.
This is the Napit version... the section on the left is for what's supplying it, as we discussed. The section on the right is for "this end" of it; I think Zd should actually say Zdb (as Zd means fault current of first fault in an IT earthing system) and Ipf should have the associated prospective fault current for the distribution circuit. I'm not overly impressed with this bit on the form, it's not laid out clearly at all!
Here's the Electraform version which is the easiest to understand of all of them in my opinion. I miss using this!
I can't tell which form you have (?NICEIC) but I suspect it is in two parts like these two above.
Cheers that helps
Reply to Filling in this part EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
You are allowed a sampling process, i feel it would be impossible to I&T every point. If the client is prepared to pay for that so be, you can use...
