S

sparks1653

hi, i have been filling out some practice certificates at work today and have some questions before i go for training. i was looking at a BS1361 main fuse,
how can you tell if it is type 1 or 2...it wasnt written on it.
what is the normal time recommended to put on a certificate of when a new installation needs to be re-tested?

thanks,
 
if domestic 10 years till next test. for fuse it should be written on it(normaly on the side), you as electrician are not supposed to touch it. if unknown write unknown
 
Last edited:
The main difference really is that a 230 volts the rupture capacity is 16Ka and at 400v it is 33Ka

The time for the first inspection is determined by the designer of the installlation, so for domestic new install it most likely be 10 yrs. For commercial/industrial it will depend on the enviroment and could be for a new install 5 yrs.

If your doing a PIR then you would take each installation at it's own merit and set up the next date on many things, enviroment, condition etc etc
 
Hi,

If the the BS1361 fuse is in single phase ( 230v ) it will most certainly be 16.5kA and that is a type 1, if its a 3 phase ( 400v ), then its 33kA and a type 2. OSG, table 7.4 page 57.


Jay
 
Last edited:

Reply to filling out certificates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
What you're trying to say, is that I've always done it correctly :)
Replies
11
Views
1K
Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top