Micky d

Hi, I am trying to replace an emergency light in a hotel but cannot isolate the permanent live. I have isolated the mains feed in from the DB but there is another PL wired in from the ceiling void. I have tried the usual isolating trips one at a time however, the board is poorly labelled and additional items have been wired all over the place. The problem is that I would normally isolate the entire board however, all of the computer systems and office is also wired on to this board so I cannot turn off the whole board.

The e/m light is the only e/m light in the room but there are over 50 individual spots in the ceiling, 20 bedrooms and a corridor full of lights (every second one is an e/m) and yes I have tried to isolate the e/m lights but this unit is still live. This PL could be coming from anywhere. As I don't fancy curly hair (whats left) can anyone advise.

cheers
 
try turning off all light mcbs (very rarely you can come across a situation where light circuits have been connected wrong and are fed from 2 mcbs Due to poor installation work !)
Also in some older properties i have seen emergency lights fed from the socket circuit (i know that wrong but thats what i have found)
 
Hi, I have tried every key switch I can find. I have also tried every trip marked up as lighting but still live. I am inclined to sgree so far with ashrow, it could be wired from a socket. I will try and switch off one at a time of the ones that aren't linked to the essential running of the hotel. Well thats most of Monday taken care of then!! Thanks guys
 
Got sympathy with your situation, we've all been there, for me , 3 choices, work live, walk away, or explain the situation to the manager and tell him you need 15 mins to isolate the circuit in question, power down your office equipment at a convenient time or the job can't be done.
 
If YOU can't isolate the permanent live, then the E.m light can't have been routinely tested.
Have you tried asking whoever is responsible for E.M testing (assuming it's done in house) and see what switch(es) they use to do the test?

Just a thought, why did they need to get you to replace the light, it must have been tested and failed??
 
They have maybe stolen a PL from next door so when their lights fail you EM light works lol

I would explain that the EM light should be fed from a local lighting circuit and it is clearly not as you have proven and it should be rectified, you will probably find that this is not the only one that is installed incorrectly.

You never know you may get a decent job out of it.................

Just another thought this light may be fed from the wrong side of one of the key switches
 
I went to replace emergency light fitting today. Turned all lighting circuits off but em light fitting was still live. Opened another cabinet to find a small fuse board with 2 breakers. One was labeled kitchen and the other emergency lights contactor.

Thought to myself " ooooh found it!!!"

Switched off 6 amp mcb only to find it was connected to contactor which isolated the whole installation.... Yikes

Had 20 people cussing and cursing me as they lost all there work on there computers
 
I went to replace emergency light fitting today. Turned all lighting circuits off but em light fitting was still live. Opened another cabinet to find a small fuse board with 2 breakers. One was labeled kitchen and the other emergency lights contactor.

Thought to myself " ooooh found it!!!"

Switched off 6 amp mcb only to find it was connected to contactor which isolated the whole installation.... Yikes

Had 20 people cussing and cursing me as they lost all there work on there computers

Ouch how did you explain that one?
 
I know what my former boss would do in such circumstance, he'd say "Stop P'ing about make it safe son" meaning short the permanent live, you soon found out which circuit, breaker or fuse it's on when somebody screamed because they lost power.
 
Last edited by a moderator:

Reply to Finding the source of a permanent live in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As you've found out, there's capacitive coupling between cores which will induce a voltage into other cores when one (or more) is fed with AC. How...
Replies
3
Views
398
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top