aaronstuart

Hi,

I have been asked to fit a cu at a small flat, no supply yet, but the wiring was done by someone else a few years ago and did a runner, but where does that leave me?

Obviously i haven't designed / erected the installation, so what would i put in the certs or is it better for me to walk away.

Regards
 
could you not just fit the new consumer then obviously test it all, then for certain areas like "cables routed in prescribed zones" etc etc, put "limited" in these boxes as you dont know. id of thought you would have to check behind accesories as well.

interesting one this wonder what others will say?

rich
 
Hi,

I have been asked to fit a cu at a small flat, no supply yet, but the wiring was done by someone else a few years ago and did a runner, but where does that leave me?

Obviously i haven't designed / erected the installation, so what would i put in the certs or is it better for me to walk away.

Regards

well to me this is a no brainer

if you use the short form you sign the block that says "I, being responsible for the design, installation etc" then you are responsible for the whole job.

if you use the long form, then someone woul have to sign for design etc (and presumably they wont be)

so, walk away, or be sure that whatever you put your name to is of sufficient standard to avoid the doo doo's hitting the fan in YOUR direction

aalthough there is another alternative

do the CU change, but only put that work on the cert. Think of it like doing a CU change on an existing property with no previous certs

so you would still check main bonding, do your tests etc, but would not be signing for the actual installation work:rolleyes:
 
It always tickles me to learn how much paperwork you guys seem to be buried in. Here in the states, I wouldn't even give a second thought to changing out the cu ("breaker box", to us here). I'd just make sure that my name was only officially associated with changing, or in this case adding, the cu. Naturally, I'd test and visually examine any portions of the existing wiring to be refed to assure that they're safe to put into use just to cover my own butt, but we're not even required to do even that much in the US.
 
On the easycerts I use there is a section
"details of the installation & extent of installation work covered by this certificate"
Where in this situation I enter installation of consumer unit only. Fit the unit test all circuits job done.
 
The general concensus seems to be ensure that your test certificate covers the cu only. Obviously you will carry out your normal tests, as Shakey says, but should you find any anomolies make sure that you inform the customer.
 
well to me this is a no brainer

if you use the short form you sign the block that says "I, being responsible for the design, installation etc" then you are responsible for the whole job.

if you use the long form, then someone woul have to sign for design etc (and presumably they wont be)

so, walk away, or be sure that whatever you put your name to is of sufficient standard to avoid the doo doo's hitting the fan in YOUR direction

aalthough there is another alternative

do the CU change, but only put that work on the cert. Think of it like doing a CU change on an existing property with no previous certs

so you would still check main bonding, do your tests etc, but would not be signing for the actual installation work:rolleyes:

OR (?)...

Fit the CU as Shakey describes and insist that you will only do the work if you can PIR the installation. That way, any remedials is more work and money for you.
 

Reply to Finishing a job thats been taking years in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K
  • Question
It's actually not as those are accidents outside of work, if you suffer an injury whilst working for someone else or doing private work then...
Replies
12
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top