leekemp85

over the last weekend I added a few smoke heads to a office. I will be submitting a modification certificate but will I also need to supply a log book could do with a quick response as I need to get the invoice in before the end of the month

thanks, Lee
 
yeah they have but I read something earlier on that said any extra work should include a new log book and it got me confused as to why??
 
You dont need a new log book, but you have to put in the existing log book any work carried out on the fire alarm system, additions, alterations etc.
 
Are sounders required on emergency exit stair's if the sound level is below 65 db type l4 system.
There are no sounders on ground floor.
When filling out the variations from recommendations bs5389 is there a code system like when doing a PIR.
Also all the earths were cut off and all alarm cables ran with the mains cables, is it worth making a note of this
 
You should obviously be aware of a fire from wherever you are in a building, Many people have cut the eraths off over the years, it doesnt hurt to have them connected but i have never come across a system that actually uses them.
 

Reply to fire alarm help in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
744
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
974

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
410
I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
434

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top