hi just been asked by the fire alarm commissioning engineers to provide them with the loop resistance values of the loops i have wired for them in a large shared housing project, can anyone point me in the direction as to what i need to do to test this and what results i need to satisfy him ? this test is normally done by the fire alarm firms i have had commissioning for me in the past so i dont want to be caught out on this or look a ****.

cheers:crazy:
 
Pos to Pos in low ohms
screen to screen (earth conductor) in low ohms
Neg to Neg in kilohms (from this they can divide value of one device into total and get approx amount of devices fitted.

There are a couple more measurements taken also.

I am a little surprised that the fire commissioning guys are asking you to do this for them, as if i was commissioning this i would not accept your readings on my sheet. But hey everyone to there own Lol
 

Reply to fire alarm loop resistance test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

ESP - https://www.espuk.com/# is the company you are referring to part of Scolmore
Replies
2
Views
366
NICEIC Certification Scheme NICEIC Competant person scheme
This sounds very similar to me. My level 3 NVQ is in engineering maintenance and I also have a HNC in Operations Engineering. I’ve been working...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top