1ManRiot

This might be a very vague question or not even have an answer or might be very specific to different sections of industry, I'm really not sure.

But is there legislation or guidelines for testing/maintenance of fire alarm systems in unmanned/unstaffed buildings?
 
According to the British Standard Code for Fire Detection and Alarm Systems for Commercial Buildings
(BS5839: Pt 1: 2002), the owner or person having control of the premises should appoint a responsible person
to oversee the effective operation of the Fire Alarm System (Clause 47.1).
Below is a summary of the main functions the “Responsible Person” is expected to carry out. This summary is
not intended to replace Section seven (User responsibilities) of BS5839: Pt 1: 2002 (available from BSI, or your
local library). It is meant to give a brief outline of user responsibilities for the safe upkeep of the Fire Alarm
System. The number in brackets shows the relevant BS5839: Pt 1: 2002 clauses.
The responsible person must:-
1. Have sufficient authority to carry out the duties associated with being the responsible person (47.2.a)
2. Check the system at least once every 24 hours to ensure there are no faults present (47.2.b)
3. Ensure there are arrangements for testing and maintaining the system (47.2.c)
4. Ensure the log book is up to date, and available for inspection (47.2.d)
5. Instruct all relevant occupants on the basic operation of the system, including start evacuation, silence
alarms, silence faults and system reset (47.2.e)
6. Take appropriate action to limit the rate of false alarms (47.2.f)
7. Ensure that all detectors and manual call points remain unobstructed at all times (47.2.g)
8. Liase with maintenance personnel to ensure that cleaning, maintenance or building work does not interfere
with the functioning and reliability of the fire alarm system (47.2.h).
9. Ensure any changes to the system are recorded with updated drawings, operating instructions etc (47.2.i)
10. Ensure that there are spare parts (especially Call point elements) held on site (47.2.j.1&2)
With the Premier SX Range of Fire Alarm Panels, we recommend the following tests are carried out: -
Daily Inspection
check that the green Power LED is lit.

If there are any yellow fault LEDs lit, or the green Power LED is not lit, report the fault(s) to the designated
site maintenance engineer.
Weekly Test (you may wish to temporarily disconnect the Aux relay during the following Tests)

Set off a manual call point or sensor to test the Fire Alarm panel responds and all the sounders activate.

Do not test the same device each week. Test a different zone each week using a different call point or
detector so that eventually, all the devices will be tested.

Reset the System by pressing 1,2,3 (Stop sounders, Silence fault tone, Reset).

Turn key to controls enabled. Press the LED Test button. Check that all LEDs light, and the buzzer sounds

Check that no call points or fire detectors are obstructed in any way. (eg New furniture or decorations)
Quarterly Test (to be carried out by authorised service personnel only)

Check that any servicing or repairs required by all previous logbook entries has been undertaken.

Visual inspection of the batteries and connections. Check the alarm sounders work on battery only.

Activate a device from each zone to test the fire alarm. (As per weekly test).
Annual Test (to be carried out by authorised service personnel only)

Check every detector, call point, sounder and all auxiliary equipment for correct operation.

Check Transformer output Voltage (32 VAC), Charger Voltage (28.4V off load, adjusted with VR1) &
Battery Voltage (25-27V)
Every Five Years (to be carried out by authorised service personnel only)

Carry out a complete wiring check in accordance with the testing and inspection requirements of the
relevant National wiring regulations (in the UK this is the IEE Wiring Regulations). The Batteries should be
replaced because SLA batteries have a working life of 5 years.
 
Hmmm that just says 'appoint someone to ensure schedule is stuck to'. Is there any specific time constraints, ie, visually inspect daily, test with smoke monthly, etc?

Surprised they need testing every 24 hours, how can that possibly apply in an unstaffed building that may only get entered monthly?
 
To the best of my belief and experience, there is no difference in the minimum specification requirements relating to unmanned/un-staffed premises, to those that are. If the building requires fire alarm protection, then all the requirements of that system must be met....
 
To the best of my belief and experience, there is no difference in the minimum specification requirements relating to unmanned/un-staffed premises, to those that are. If the building requires fire alarm protection, then all the requirements of that system must be met....
Makes sense logically...
 
Still looking for answer, but we have a communal Fire Alarm System consisting of 4 Zones in which includes 5 Units occupied and 1 Storage.We test 2 call points weekly ,and record it. Obviously in different Zones. If a fault shows up on the panel you will get a warning beeping,But you need to check it , depending on what you are protecting from fire.
 

Reply to the thread, titled "Fire alarm testing in an UNMANNED building" which is posted in Security Alarms, Door Entry and CCTV (Public) on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fire alarm testing in an UNMANNED building
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
1ManRiot,
Last reply from
Electro-tech,
Replies
6
Views
2,481

Advert

Back
Top