Fire Damper Actuators | on ElectriciansForums

Discuss Fire Damper Actuators in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Arms
Joined
Jun 2, 2018
Messages
437
Reaction score
336
Location
Newcastle Upon Tyne
Hello

Working on a site with dampers fitted on the ducting which need fire shut offs connected to the fire panel via an actuator.

The actuators have 4 contacts “Damper Closed NO and NC” and “Damper Open NO and NC”.

Presuming they need a NC contact so the actuator operates and closes the damper when the alarm goes off but not sure which NC contact to utilise.

Any insight appreciated.

Thanks.
 
Hi, It sounds that what you have described are the monitoring contacts that would send a signal to a Building Management System or a mimic somewhere that indicate the position of the dampers at any point of time. There should be terminals for the coil, possibly 24v, which would be fed from a power supply unit which would have a fire alarm output module which would change status when the alarm sounds. It may well be a NC set of contacts in the fire alarm interface which hold the dampers open against a fail safe spring so if it looses power it will automatically close.
 
Hi thanks for the reply

Yes so it’s a 24v power supply required, wasn’t sure if there was anything specific that would be required or would a bog standard 24v PSU suffice?

So if the 6 cores are for signalling as you say, would it be feasible to switch the power going to the 24v PSU through a contactor with the coil being supplied by an auxiliary relay on the fire panel?

Thansk
 
Hi thanks for the reply

Yes so it’s a 24v power supply required, wasn’t sure if there was anything specific that would be required or would a bog standard 24v PSU suffice?

So if the 6 cores are for signalling as you say, would it be feasible to switch the power going to the 24v PSU through a contactor with the coil being supplied by an auxiliary relay on the fire panel?

Thansk
As far as I am aware, any 24v power supply would be suitable, but in particular one designed for fire alarm and includes facilites for back-up batteries to be fitted as otherwise you would need to reset the unit after a power supply.

Yes, the unit would be switched via a relay in circuit with the 24v line off the aux relay on the fire alarm panel, assuming that is a convienent place to pick up a switched contact.

Unless you need monitoring you would not need to connect the 6 wires to anything.
 
As far as I am aware, any 24v power supply would be suitable, but in particular one designed for fire alarm and includes facilites for back-up batteries to be fitted as otherwise you would need to reset the unit after a power supply.

Yes, the unit would be switched via a relay in circuit with the 24v line off the aux relay on the fire alarm panel, assuming that is a convienent place to pick up a switched contact.

Unless you need monitoring you would not need to connect the 6 wires to anything.
Evening,

OK great, well that’s good to know as I initially thought id need a 2 core cable back to the fire panel from either the NO or NC cores of the 6core.

But now if I wire the supply through a contactor which is switched via a NC relay, I only have a 230v cable to pull over to a 24v PSU adjacent to the actuator.

Would the 24V supply having a battery backup not stop if from closing as it would never lose power?

I’ve attached the wiring diagram if you’re able to take a look and just confirm your still happy that it is what you think?
 
this is one of those where nobody has all the information.

it depends on
why it is being installed
who is designing the system
what standard the designer is hoping to achieve.

in an ideal world, the person ordering the work would give you all the information at quote time and ask if you can provide to that standard.
 
this is one of those where nobody has all the information.

it depends on
why it is being installed
who is designing the system
what standard the designer is hoping to achieve.

in an ideal world, the person ordering the work would give you all the information at quote time and ask if you can provide to that standard.
Very rarely is a job carried out in an ideal world!

Only info given to me was that the ventilation will have 2 dampers which need to close when the FAP goes into alarm.

Best thing I have to go on so far is manufacturers guidance for their product.
 
What was the make and model by the way?! What type of fire alarm too, most addressable systems you can simply add a relay output module to the loop near the equipment to be operated, some modern bi-wire systems now have this ability too.
 

Reply to Fire Damper Actuators in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Commonly known as double knock, some pirs have a latch on time delay for a few seconds, giving time for the 2nd one to activate .
Replies
3
Views
374
  • Question
Just an heads up here, any expansion or addition to the control system of a Fire Alarm should be suitable for the job in hand and I don't mean...
Replies
8
Views
1K
Darkwood
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top