If the cables came through a pink 15mm fire board then yes maybe the hole around the cables should incorporate a fire barrier but not the rear entry of the enclosure.
Agree, I would not fire seal the board.yes i Think the plaster board should be repaired if it’s been hacked.
but the actual consumer unit doesn’t require mastic
I'll chuck 527.2.1 into the mix.
Where a wiring system penetrates any building element that has a prescribed fire rating it should be sealed back to that rating.
Not to do with sealing a CU, but maybe the wall behind it if it needs to be. Rear entry penetrations I'm on about.
A dwelling is usually a single fire compartment, if however pink board is used say in the attached garage with a bedroom above, that would indicate a separate fire compartment especially if there’s a fire door involved somewhere, so penetration of that compartment would need fire sealing.All plasterboard has a fire resistance of 30mins no matter what colour is, some times a double layer of standard white plasterboard is used to achieve the required rating, so the colour is not a good indiction of what the requirement is or that it is a fire barrier.
The plasterboard is fixed to the I joists to form the ceiling , that’s it, lam beams etc do not get covered in plasterboardI tend to disagree. Whilst a domestic property is usually classed as one fire department, try building a house without covering structural timbers and joist etc with plasterboard and expect to have it passed by your LBC.