Done a fuseboard change today, but getting a bit confused with the Ze and Zs tests
Where are these tests done? At the DB main tails incomer, at the origin (sweated earth on incoming cable)
It is a TN-S supply and i have a 3 lead L-N-E megger loop tester.
Getting a bit confused aswell with what bonding is disconnected too.
Any help would be appreciated. Thanks.
 
The installation should not be energised till all tests are completed but just in case, Turn off, prove dead, disconnect main earth hook that up to your earth croc. Put neutral probe on neutral terminal and live probe on live then press the button the result given is Ze.
Zs is done at each point of utilisation in a similar manner with the highest reading being the one you record.
 
YEs this is a test of the circuit loop impedance which is carried out at the last point of the circuit or the mid point of the ring it is also carried out after the r1r2 test which on a lighting / radial circuit should be carried out at every point to confirm polarity at each point
 
dont forget here as well 067256......that you will need to test twice for a single phase supply.....once for line-earth...a Ze..this will give you your PEFC at the origin of supply...and another for line-neutral...this will give you your PSC at the origin of supply and it is the HIGHEST of these two measurements that will be your PFC that you record......
 

Reply to First proper test and inspect today. Confusion. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top