S
Spoon242
Guys,
I have just been working through a TT system round an old work colleagues home as it has given me the opportunity to look into TT's.
He has a the incoming supply through a 100mA switch which carries on in to a 10 way Wylex board in the house with BS 3871 breakers and its own main switch.
I took my Ze by isolating the house removing the main earth cable from the MET and using my Fluke 1653, on no trip Ze, took the reading. Result was 530 ohms. From looking at the regs I can see this is high, as a 100mA should be 500 ohms, ideally 200 ohms, Table 41.5.
Do I need to remove his earth spike and renew it, or add an extra spike as a course of action.
Secondly, Zs readings for the house circuits are taken in the normal way I'm assuming, but of course I'm getting readings like, for example,
Cooker 508 ohms
Induction hob 501 ohms.
Im thinking these are high, please slap me in to shape on this, and ten worse what tables do I look the max Zs up in for TT's
Bloody 2391 was always geared up for TN system Grr!
Thanks in advance for your help as always.
I have just been working through a TT system round an old work colleagues home as it has given me the opportunity to look into TT's.
He has a the incoming supply through a 100mA switch which carries on in to a 10 way Wylex board in the house with BS 3871 breakers and its own main switch.
I took my Ze by isolating the house removing the main earth cable from the MET and using my Fluke 1653, on no trip Ze, took the reading. Result was 530 ohms. From looking at the regs I can see this is high, as a 100mA should be 500 ohms, ideally 200 ohms, Table 41.5.
Do I need to remove his earth spike and renew it, or add an extra spike as a course of action.
Secondly, Zs readings for the house circuits are taken in the normal way I'm assuming, but of course I'm getting readings like, for example,
Cooker 508 ohms
Induction hob 501 ohms.
Im thinking these are high, please slap me in to shape on this, and ten worse what tables do I look the max Zs up in for TT's
Bloody 2391 was always geared up for TN system Grr!
Thanks in advance for your help as always.