aaronstuart

Hi,
If you're adding any accessory, extra socket, light etc, do you heve to upgrade tails to 25mm and earth to 16mm, if they are only 16mm and 10mm? Or can you just note it down on Minor works cert if client doesnt want the work undertaking?

Thanks in advance
 
elecsa told me if doing any minor works you don't have to upgrade tales or bonding if its a minimum of 16mm for the tails, 10mm main earth and 6 mm to gas and water.
 
Previous post ^ above pretty much sums it up - as, by its nature, most Minor Work is not going to add significantly to the overall loading of the tails, then providing existing are atleast 16mm there wouldn`t normally be a requirement to increase their size - even if the DNO insists they should be 25mm or more. As many distributors won`t sanction us to upgrade anyway, & they don`t seem to be exactly rushing to upgrade all the puny tails still in existance themselves, you`re left to think "why should i worry?". If you`ve informed the customer of the current requirement of 25mm min but they`re not willing to pay you to do what the DNO should be doing then you`ve done all you can.
However, this regulatory body approved guidance presumes that the person carrying out the work has reasonably assessed the existing installation as being safe to carry the likely load. If you haven`t you`d be fairly considered negligent in re-energising after adding further loading. Remember, we can`t leave the installation in a less safe condition in which we found it...
 
Last edited by a moderator:
Always happy to help.

& the button over there >>> always leaves a warm fuzzy feeling ;) >>>>>>>>>>>>>>>>>>>>>>>>v
 
Last edited by a moderator:

Reply to Fitting a socket? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
523
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
929
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
354

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top