Hi all
So had some issues lately related to high current fittings .. dp switches mostly.
A number of electric boilers of various ratings .. from 7kw on up burning out their isolators .. the last one this week was a 7.5kw electric boiler running on a 6mm t&e cable 4m long from a 32A MCB .. 50A dp switch isolator.
No sign of cable overheating at the boiler (even though the terminal block is by the output pipe) . No sign of cable over heating at the consumer unit.. no tripping of the 32A mcb ..
So I understand the the cable is rated to carry over the 32.5 ish A which is max load .. mostly the boiler is modulating and no using anywhere near full power.
Now i know that there are issues with various 13A sockets that are not rated to supply 13A continuously 24 7 .. and these have caused problems with things like car charging.. we use all Hager fittings which I believe are all rated for continuous duty of there rated current... but many manufacturers sockets are not .. my question is are many dp switches and other fittings not rated for continuous duty at their started rating.. and this is causing them to fail at much lower loadings .. and if so how do I find out the continuous duty rating of such fittings.. I believe they should be published ..but a quick search tonight I can't turn up any ratings.
I know at the installation stage it's easy to over rate these things .. which I guess is why the installer for the 7.5kw boiler fitted a 50A dp switch .. but it still failed.
All thoughts greatfully accepted
Ta
Vito
So had some issues lately related to high current fittings .. dp switches mostly.
A number of electric boilers of various ratings .. from 7kw on up burning out their isolators .. the last one this week was a 7.5kw electric boiler running on a 6mm t&e cable 4m long from a 32A MCB .. 50A dp switch isolator.
No sign of cable overheating at the boiler (even though the terminal block is by the output pipe) . No sign of cable over heating at the consumer unit.. no tripping of the 32A mcb ..
So I understand the the cable is rated to carry over the 32.5 ish A which is max load .. mostly the boiler is modulating and no using anywhere near full power.
Now i know that there are issues with various 13A sockets that are not rated to supply 13A continuously 24 7 .. and these have caused problems with things like car charging.. we use all Hager fittings which I believe are all rated for continuous duty of there rated current... but many manufacturers sockets are not .. my question is are many dp switches and other fittings not rated for continuous duty at their started rating.. and this is causing them to fail at much lower loadings .. and if so how do I find out the continuous duty rating of such fittings.. I believe they should be published ..but a quick search tonight I can't turn up any ratings.
I know at the installation stage it's easy to over rate these things .. which I guess is why the installer for the 7.5kw boiler fitted a 50A dp switch .. but it still failed.
All thoughts greatfully accepted
Ta
Vito