I have been wiring up a workshop for a customer, and went back the other day and he had bought 4 16A 110v sockets, and a fixed 3kva transformer

He wants me to wire these 4 off 1 transformer. So I have wired the transformer into the board, to go on a 16A supply.

At the 110v side am i right in saying the cable i use would have to be able to take about 28A? (3kva at 240v=13A, 3kva at 110v= 27A) I thought it would have to, but portable trannys have leads with 1.5mm cable so i'm not so sure

Never come across 110v fixed installations before so i'm just a bit confused about this :confused:
 
Check that the transformer secondary has a centre tap and this MUST be connected to earth if no centre tap then this transformer is unsuitable for workshop use as fault voltage will be above 55v
 
What about the cable sizes?

And i guess the cu would have to be adapted, 2 55v into the main switch, then 2 out to feed each 2pole mcb?

If you have 2 x 55v secondary windings these should be connected in series and joint between the windings connected to earth the other ends of the windings will go to the main switch on you DB

The earth tap will only allow a voltage of 55v to earth under fault conditions
 
Last edited:
If the secondary is a single winding for the 110v there will / should be three terminals one will be labelled centre or CTE the other two will indcate voltage as 0v and 110v alternatively it will indicate 55v between centre connection and each of the other two connections
 
ya 2 phase colours and earth for the 110v sockets(for 55-0-55)

if the trafo needs overload protection sometimes it can be fitted at the 110v board.

rcd as well if required(dunno what the rules are in the uk for reduced low-voltage)
 
Last edited by a moderator:

Reply to Fixed 110v installation in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Except where provided by the EV charging equipment, protection against DC fault currents shall be provided by: (i) an RCD Type B, or (ii) an RCD...
Replies
5
Views
925
  • Question
You’ll need level 3 qualifications- 2391 or equivalent plus 18th edition to get on an PV course. To join a scheme and sign work off, I think...
Replies
1
Views
516

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top