It’s a long time since passed my domestic and industrial apprenticeship and renewed my 16 Edition. I have not worked in the field as a sparky since 1984.

I have just had a FWT completed on a house I own and done by an electrician i don’t know. He has quoted a C2 on the form. In general all good but with with exceptions to additional spurred sockets added to 2 ring main circuits and then in the testing Schedule A section 5.5 Adequacy of cables for current-carrying capacity with regard for the type and nature of the
installation (See section 522) C2 Yes.

I was not aware that there was a restriction on the amount of spurs on a ring main providing you don’t go over the amount of actual sockets on the ring?

Can anyone clarify or am i way off the mark?

Thanks

Biffa
 
The total number of unfused spurs cannot exceed the total number of points on the ring.

An unfused spur must only feed 1 point (single socket, twin socket or fused spur each count as 1 point)

An unfused spur must be minimum 2.5mm cable if T&E.

To give a C2 the item must be potentially dangerous, not just non compliant.
For example if you have a spur which feeds a SFCU for the boiler (3A fuse) and another SFCU for an external light (3A fuse) then it does not comply but is also not potentially dangerous.
 
Thanks for the answers and questions. I have actually got to the bottom of it. It is a SPUR of a SPUR, which I know you cant have. I have three options

1 One option is to derate the ring circuits and treat them as radial circuits, which would involve de-rating the current 32A circuit breaker to a 20A circuit breaker, this would deb a like for like swap. Under normal load conditions this arrangement should be satisfactory.

2.The more disruptive option is to introduce fused connection units where there are more than one spurred outlet.

3. The third option is to disconnect the additional outlets and replace with a blanking panel

Which would be best?
 
Thanks for the answers and questions. I have actually got to the bottom of it. It is a SPUR of a SPUR, which I know you cant have. I have three options

1 One option is to derate the ring circuits and treat them as radial circuits, which would involve de-rating the current 32A circuit breaker to a 20A circuit breaker, this would deb a like for like swap. Under normal load conditions this arrangement should be satisfactory.

2.The more disruptive option is to introduce fused connection units where there are more than one spurred outlet.

3. The third option is to disconnect the additional outlets and replace with a blanking panel

Which would be best?

If you can, change the first socket to a FCU
 

Reply to Fixed Wire Test. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top