Sonor

Hello

I've been asked by a client to rectify the problems discovered after a fixed wiring report on one of their retail buildings.

The report states that "No RCD protection for all sockets rated up to 20A", Apart from any sockets located exterior to the building which are on RCD's.

I was under the impression that this mainly applies to domestic properties where the occupant is classified as an "ordinary person".

When it came to commercial property as long as there are "instructed people" this reg did not need to be applied.

It seems to me that it's a bit of a grey area as instructed persons would need to understand the EWR1989 and the operation of electrical regulations BS EN 50110 for the regulation not to apply.

Now in reality, while management of the retail building may have been given training with regards to EWR1989/BS EN 50110, I doubt they would be able to remember much of it.

Secondly, they have cleaners that use the sockets and they seem to be classed as ordinary persons, there is a cafe with WIFI, but customers are not allowed to plug their laptops into sockets.

Is the test and inspection company being overly cautious?
 
Sonor,
411.3.3 [additional protection for socket-outlets not exceeding 20A, used by ordinary persons] is not specific on location. It is a means of additional protection. This is further detailed in section 415

Are you getting mixed up with Part P?

Hope I haven't offended you!

AIM
 
AIM, thanks for your reply, no you haven't offended.

I thought it was to do with Part P only as well, but they have flagged this on a commercial property and when I checked out some ECA info on it, it said if EWR1989 and BS EN 50110 are applied and the "instructed person" is adequately advised then this reg is generally not applied.

But being a commercial property it means public enter the building. I personally think it's the testing and inspection company going over the top.
 

Reply to Fixed wiring report results...can anyone help? in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

And learning I am ☺️ if I didn't have the limited knowledge I have at the mo I probably wouldn't give it a second thought but as I do and have a...
Replies
15
Views
4K
Hi, My probe was on the outgoing neutral of the RCBO. I will be testing again this week so I will play around, many thanks for your reply.
Replies
7
Views
4K
W
NICEIC Certification Scheme Help interpreting NICEIC report
"Borrowed neutrals present a significant danger to anyone working on the circuits affected, it has never been permitted in the regulations as far...
Replies
19
Views
3K
Ooohhh, someone is tired aren't they!
Replies
57
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks