J
jerriais
Hi,
On a recent installation a new subbie wired up 1 string of 16 (CS6P-250P) where there should have been 2 strings of 8. Scaffolding came down yesterday but now system has an over-voltage shutdown, not surprising really.
Question is ... can it be fixed by asking them to split the incoming single string into 2 in the loft? It seems that this would halve the voltage and solve the problem, it is a dual MPPT inverter (SB 3600TL-20) but no shading so not a problem if independent MPP tracking is no longer possible. The max system voltage of the single string will be 668V which is within the panel and cable limits (1000V IEC) so I don't see any problem. Am I missing something? It almost seems too simple. Obviously I'd rather do it this way than get the scaffolders out again and rewire on the roof.
Cheers,
Matt
On a recent installation a new subbie wired up 1 string of 16 (CS6P-250P) where there should have been 2 strings of 8. Scaffolding came down yesterday but now system has an over-voltage shutdown, not surprising really.
Question is ... can it be fixed by asking them to split the incoming single string into 2 in the loft? It seems that this would halve the voltage and solve the problem, it is a dual MPPT inverter (SB 3600TL-20) but no shading so not a problem if independent MPP tracking is no longer possible. The max system voltage of the single string will be 668V which is within the panel and cable limits (1000V IEC) so I don't see any problem. Am I missing something? It almost seems too simple. Obviously I'd rather do it this way than get the scaffolders out again and rewire on the roof.
Cheers,
Matt