Any ideas on this one?
I am doing a survey/eicr on an intake serving 9 flats belonging to a local housing authority. The cables are early 70's 16mm/6mm T&E run through the building structure. I have assumed the maximum draw is around 30A per flat and checking the Ze values and distance it appears the cpc is of adequate size using the adiabatic equation. The issue is each flat runs through a 60A switch fuse isolator housing 60A 3036 fuse before terminating into a 3 phase ryefield housing what appears to be a bs88 Gg 60 70's fuse per flat.
Which fuse do i use for the adiabatic calc and am i correct in saying i have a discrimination issue between the fuses here? code 3 on the eicr?
I am doing a survey/eicr on an intake serving 9 flats belonging to a local housing authority. The cables are early 70's 16mm/6mm T&E run through the building structure. I have assumed the maximum draw is around 30A per flat and checking the Ze values and distance it appears the cpc is of adequate size using the adiabatic equation. The issue is each flat runs through a 60A switch fuse isolator housing 60A 3036 fuse before terminating into a 3 phase ryefield housing what appears to be a bs88 Gg 60 70's fuse per flat.