looking at table 4F1A, insulated flexible cables with sheath:

6mm 2 core will carry 39A, volt drop 7.8 mV/A/m

6mm 3/4/5 core 34A, volt drop 7.8 mV/A/m

these are non-armoured flex.
 
4mm flex will carry 32 Amps.

I'm assuming you mean common flexible chord, Table 4F3A

I'm glad you've said that, I was looking at that table first, however, whats the difference between that and the table I stated from?? I assumed that was the old twisted flex you used to get on pendant drops.
 
Now you've done it Roukel,

We now have to have a debate on what's a flexible cable and what's a flexible chord, and the difference between the two.

Let me start,

I've no idea.
 
Just look in Part 2 (definitions) in ol' red.

Basically a flexible cord is the same as a flexible cable BUT the CSA of the coductors doesn't exceed 4mm. Make of that what you will.:rolleyes:


Never really thought about it before.


Edit.....The tables start at 0.5mm for cords and at 4mm for cables, but 4mm appears on both with different values, must be temp corrected on one.
 
Last edited by a moderator:

Reply to Flex rating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
And have a very merry Christmas and a great new year all
    • Friendly
    • Like
Replies
2
Views
102
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
730
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
1K

Similar threads

G
  • Article
Radiator flex pipes Could I pull these flex pipes up by cable tying them onto the back of the radiator (it’s a double rad) Just wondering if the...
Replies
0
Views
136
Glasgowman
G
S
  • Article
Flex or non-flex adhesive for sticking backer boards to masonry wall? Just wondered what would be best? The original tiles had a few hairline...
Replies
0
Views
290
Stoobloo
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top