davek

Hi all
Any suggestions, for dealing with flood damage circuits the property had a leak on the bath now one of the circuits is tripping randomly I have IR the circuit and it is giving a 000 reading tried splitting the ring but with little success on establishing exact location its a very old house lost of added spur sockets two adjacent to the bathroom where the leak was. The boiler is also on this circuit but on a plug top so I have ran an Extension to it, and have put heating on full.
IR L-N 88.8
L-E 000
N-E 89.2
on The other side of ring
L-N 000
L-E>500
N-E>500
 
Yep, you could rather say I've got the t-shirt when it comes to floods. Time and gentle heat is your saviour, once its dried then change any affected accessories as you can be left with internal corrosion on the switch contacts.

What you have to ask yourself is this: what condition was it probably in already, BEFORE the water?!
 
Yep, you could rather say I've got the t-shirt when it comes to floods. Time and gentle heat is your saviour, once its dried then change any affected accessories as you can be left with internal corrosion on the switch contacts.

What you have to ask yourself is this: what condition was it probably in already, BEFORE the water?!

hang on, i;ll ask Noah.
 
Tel, down here where I've been doing all the uninsured flood repairs (costs being picked up by the Govt) in three old places I've had to rewire top to toe even though there was only 4-5" of water in the place originally, simply as they've been in such a bad state to start with my hands were tied.
 
cheers Guys strangely I missed the call on this one but rang the letting agent back but had given the job away. feed back off tenant was he said he cant do much as its working now de to them resetting breaker lol. My thoughts is a jb as I took bath panel off to see if any leaks still present and its one of those old terraced that have multi levels upstairs, and could see socket spur cable dropping down under bath floor, so more than likely a jb under there. Also bet there are interconnecting ring but not check yet more concern with the IR
 

Reply to flood damage electrics in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from...
Replies
4
Views
528
davesparks
D
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
760

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top