I HAVE A PROBLEM I WANT TO WORK OUT LOAD ON A FOOTBALL PITCH LIGHTING
Philips ‘OptiVision’ MVP507 2KW Floodlight. there are 72 no off lights they are 400v 2 phase
the load is split over the three phase i though it would be 72 * 2ooow = 142000 so142000/400v=355 355/3= 118.33 amps but it is taking around 200 amps per phase
any ideas
 
Last edited by a moderator:
Welcome to the forum Marty. You've put your question in the wrong section but I'll ask a couple of the lads to have a look at this instead of me making an half arsed attempt. (i get it at 208A but I'm not 100% sure so I won't put up my findings).
 
think paul's got ot . 72 x 2000 =144000 divide by 400 = 120A then there's the ubiquitous root3 gives us 207.84A

THat's about right - the calc is P = U * I * sqrt(3) * cos(phi) - where sqrt3 is angle of rotation and Cos(Phi) is inductive load factor - from memory.

For resistive loads like a floodlight, Phi will be zero. For inductive loads, such as flourescents, is can be around 0.95 or so.

Square root of a nominal 415V is 1.732., so:

144,000/(415*1.732) = 200.57A nominally. These are RMS values, by the way.
 

Reply to flood lighting problem in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top