Hi chaps,
a friend of mine has quite a few Fluke 1652's , I myself always use Megger.
My nephew now works for his firm, and uses as I do a 1552.
On testing a block of flats he gets readings in excess of 17ka (low eli etc)
His boss tells him the meter isn't giving the correct reading.
I have had on quite a few occasions high pfc's and have given reasons as to why you can have such readings, obviously there is a transformer close by, and being a council install, has an excellent spec.
Also, told him that the readings are more likely to be in the region of 7ka due to inherent character of the meter.
The thing is,,, his boss's meters never give a reading more than 4ka
He has about 30 lads and like I say, they never go over the 4ka mark.
I'm not sure about Fluke, but when testing do they have to do anything different, ie, join e-n leads or is the 20a rather than 25a test current anything to do with it ?

I know I'm right, but at the same time, my friend, who's been in the game as long as I have, is adamant that my nephew isn't testing correctly.

Can any body shed some light on Fluke testers and testing efli - pfc

CHEERS :eek:
 
Hi..........lets see if this helps you understand what reading you should be getting. Take your Ze reading and a good reading would be say 0.06 ohms

230v divided by 0.06 ohms = 3833A or 3.8 ka

So a reading of 17ka seems very high to me too

Mark
 
Have you ever tested between phases on a Three phase system ?


How do you test between phases? for your PFC.

My understanding of the test is........ Test all the phases to earth and the highest PFC is multiplied by 2.

There isnt to my knowledge an actual 3 phase test with the fluke meter?


Mark
 
Mark, I should of elabarated that remark, " have you ever tested between phases on a Three phase system using a Megger 1552 ? "
 

Reply to fluke 1652 pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
252
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top