Fluke 1653 mft??? !!! | on ElectriciansForums
Discuss Fluke 1653 mft??? !!! in the Electrical Tools and Products area at ElectriciansForums.net
W
Wingnut
Hi guys,
I need help with my new 1653 mft, Which reading do i use for Ze, & which is Zs i don't seem to be able to work it out!!!
Is it me or am i reading it wrong ?
Never used the 1653. All the testers I have used, use the same setting for Ze (earth disconnected) or Zs (earth connected).
My tester (Meggar MFT 1553) does have a No trip setting and 25A setting for getting Ze/Zs. The No trip is for use when you will be testing a supply fed from an RCD (and you must use L,N,E leads), opposed to the 25A setting for testing circuits fed from a normal MCB/Fuse (then only the L&E lead can be used).
Youtube might have a video of it on there???
not used the fluke, but from a previous thread, i seem to remember that it has a Z1 setting or something similar. have you not got the instuction manual???
Reply to Fluke 1653 mft??? !!! in the Electrical Tools and Products area at ElectriciansForums.net
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Well done. Leads sound a bit high btw mine are 0.07 when warmed up. Rcd uplift - I either calculate Zs, or use the kitcher trick. See