Hi, need some advice on testing with the fluke 1652c as had a few people show me different ways on how to do Ze at origin, PFC and PSCC
Ze at origin 3 lead test with main earth disconnected to remove parallel path, fluke set to no trip, then between incoming live, neutral and earth
PFC reconnected main earth then 2 lead between live and earth or 3 lead then test between live, neutral and earth then you press one of the functions to reveal KA or work it out from amps that come up ie 777A will be 0.78 KA rounded up
PSCC with earth connect back aswell either 3 lead or 2 lead between live, neutral seen some people do 2 lead and some people 3 lead with earth and neutral on neutral terminal and live on live
Thanks
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Fluke testing problems
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
Bradley6969,
Last reply from
davesparks,
Replies
1
Views
874

Advert

Back
Top