R
Ronyg
I was wondering how much, or if any fault current fluorescent light fittings produce, it's just that I have 16 to fit in one area and was wondering If protecting them all with one 30ma rcd and separate mcb's would cause nuisance tripping.
Depends on the circuit. Run a pefc and pscc test.
*Edit* maybe I'm not understanding the question, if you mean earth leakage current then it should be zero but if it's electronic ballasts with internal surge arrestors there may be around 1mA(ish) per fitting.
had same problem. 10 twin 5' fittings ona RCD was OK. added the last 2 fittings and RCD tripped as soon as the lights were switched on. fortunatley, the supply was a temp. builders supply. finished install had no RCDs on lighting.
Reply to fluorescent light fault current in the UK Electrical Forum area at ElectriciansForums.net
Not to mention welding switch contacts together and wondering why when they thought they had got the wiring sussed the light will still not switch...
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...