This dosn't include supply cables there is strict regs stopping me from running the Micc's up the shaft only usually lighting for shaft and lift control loom all off secondary side of lift controls.
What is the big no-no about runing the lift supply cable(s) in the lift shaft then?? Can't be anything to do with fire regulations...
Lift shafts are generally classified as CB2 fire propagating structures due to the chimney effect and therefore any cabling requires special protective measures eg. MICC to BS EN 60702 and/or fireproof shutters, ducts, troughs, trunking, barriers, fire detectors, etc. BS 7671:2008+A1:2011 422.5, 528.3.5 and Appendix 5C; BS 5655 and BS EN 81-1 apply.
Just hope the fire doesn't start in the mains room, or people could get stuck in the lift
(Assuming both supplies originate here and and back supply would be switched from here)
Just hope the fire doesn't start in the mains room, or people could get stuck in the lift
(Assuming both supplies originate here and and back supply would be switched from here)
An automatic fire extinguish system is fitted in the mains room and the isolators are at opposite ends so any fire when its all up and running of independant supplies shouldn't take out both supplies also its under caretaker control and no storage or anything flamable is allowed in the room and its a concrete ceiling so all been considered ...even in the worse case their should be ample time to evac' the building even with slower timing thats expected when mental health patients and disabled are present, none of this existed prior to the new build fire escape so anything is an improvement.